Combined more than 12 lights and plugs per circuit with load current doesn’t exceed 80%

Question Icon
Posted by: from Oshawa
2/11/2021 at 11:45:35 AM

Can following pass Ontario electric inspection on single 15A circuit break?

- 29 pot lights, 9 watt each

- 1 strip led, 15 watt

- bath fan, 72 watts

- 6 plugs

Known current is 28x9+15+72=329 watts, 6 plugs x 1.5A (rule of thumb) x 120V => 1080 watts. Total wattage is 1419 which is less than 1440 (15A*0.8*120).

If above is ok, can I add an additional GFCI receptacle on same break?

REPLIES (3)
User Icon
Leon from Protech Electric in markham
Date/Time2/11/2021 at 1:02:45 PM

Yes, I think so.

User Icon
Date/Time2/13/2021 at 7:11:28 AM

Short answer NO. When you add plugs you go back to 12, plugs are a unknown load.

To be sure, code may have changed,ask esa, the inspector has the last word.

Hope this helps,

User Icon
Date/Time3/3/2021 at 9:06:49 AM

The answer is no. As soon as you add one receptacle on the circuit you are limited to 12 devices in total.

Cheers

John Kuehnl-Cadwell, CD, ME

Master Electrician

Datawise Solutions Inc

Search the TrustedPros directory and discover the best contractors in your area.

Find your home service pro
Great renovations start with a great contractor.

Since 2004, TrustedPros has been helping homeowners find the right contractor for their home improvements and repairs.

Post Your Project

Within hours you'll be comparing offers from top-rated professionals. It's free to post and you're under no obligation to hire.

 
Trustedpros Inc. does not warrant the accuracy, completeness, safety, legality or usefulness of any Content, or Whether Content is Current and up-to-date, and TrustedPros Inc. Shall have no liability whatsoever with respect to your use or reliance upon any content or for content being removed or otherwise ceasing to be available. Please refer to the terms and conditions of use of this websites for more details.
Categories

Get quotes from top-rated contractors

x